If you do not have external reasons to use SS then ASTM A106B should be OK. I would try to limit flange connections and would not used srewed at all. Check that valves are for hydrogen service. Where possible run the pipe so that it is protected.

You do not want to have leaks. X ray may not show small pinholes. Well run hydrotest should help. If area is critical start looking helium test.
_________________________
Regards,

Jouko