#7592 - 08/22/00 05:48 PM Tank H/D ratio
BRKSNL Offline
Member

Registered: 08/22/00
Posts: 1
Loc: chicago, IL, USA
I would like to know is there any upper limit on tank height and H/D ratio.

In one of our power plant we are increasing the height of diesel fuel tanks to 22 m and daimeter to 17m due to space constraints.

Can any one advise me and tell the reason the restriction if any.

Top
#7593 - 08/23/00 01:43 PM Re: Tank H/D ratio
Richard Ay Offline
Member

Registered: 12/13/99
Posts: 6226
Loc: Houston, Texas, USA
I know of no explicit limit on the H/D ratio in API-650. However, Section 3.6.5 does warn that if the "L/H" ratio exceeds 2, then an elastic analysis must be performed to show that the computed circumferential stresses are below the allowables given in Table 3-2.

In the above ratio, L = SQRT( 6 * D * t ) if using English units and L = SQRT( 500 * D * t ) if using SI units.

------------------
Regards,
Richard Ay (COADE, Inc.)
_________________________
Regards,
Richard Ay - Consultant