#3806 - 09/19/05 05:45 AM spring hanger hydro allowable - 1.5 or 2.0 the rated load ?
sam Offline
Member

Registered: 02/25/04
Posts: 643
Loc: Maharastra, India
If a spring hanger is designed as per MSS-SP-58 & 69, what hydrotest load is normally expected to be safely carried by the locked spring hanger ? Will it vary, if the piping is designed as per ASME B 31.1 or B 31.3 ? We consider 1.5 times the rated maximum operating load for spring hanger for B 31.1 & 2.0 for B 31.3, if the vendor does not provide any figure; if the vendor provides a better figure, it make our hydrotesting simpler & we may use less temporary supports than otherwise required.

regards,

sam
_________________________
_

Top
#3807 - 09/19/05 07:04 AM Re: spring hanger hydro allowable - 1.5 or 2.0 the rated load ?
JMD Offline
Member

Registered: 09/02/03
Posts: 8
Loc: Madrid, Spain
Hello, SAM:
According to MSS-SP-58 (paragraph 10.1.2 & 10.1.3) both variable and constant spring hangers shall be capable to support up to 2 times the normal operating load.
Some manufacturers guarantee that variable and constant supports with their travel-stops and all their components, shall be capable to withstand an equivalent load in hydrotest of two and half times the operating load.
Regards,
JMD
_________________________
JMD

Top
#3808 - 09/19/05 07:19 AM Re: spring hanger hydro allowable - 1.5 or 2.0 the rated load ?
JMD Offline
Member

Registered: 09/02/03
Posts: 8
Loc: Madrid, Spain
Sorry, I have forgotten to add something.
I have not found any reference in B31.1 & B31.3 regarding to minimum hydrotest load to accomplish by support device.Only a link to MSS-SP-58.
In my opinion the requirement shall be the same indepently of which of this codes we are using.
Regards,
_________________________
JMD

Top
#3809 - 09/20/05 04:15 AM Re: spring hanger hydro allowable - 1.5 or 2.0 the rated load ?
sam Offline
Member

Registered: 02/25/04
Posts: 643
Loc: Maharastra, India
Thanks, JMD, for your reply.

From clause 321.1.3 of ASME B 31.3: 2002 edition, I considered that this clause of stresses for pipe supporting elements cover variable and constant effort spring hangers except springs.


regards,
sam
_________________________
_

Top



Moderator:  Denny_Thomas, uribejl 
Who's Online
0 registered (), 51 Guests and 0 Spiders online.
Key: Admin, Global Mod, Mod
April
Su M Tu W Th F Sa
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30
Forum Stats
12065 Members
14 Forums
16973 Topics
75151 Posts

Max Online: 303 @ 01/28/20 11:58 PM
Top Posters (30 Days)