1.As you might have noted, B 31.3 stipulates the minimum test pressure requirement as a function of design pressure. It also states that the test pressure shall be such as not to produce stress in the piping exceeding material yield strength (the minimum of the yield strengths of the two materials in question, in your case) at test temperature etc……This directs you to the maximum test pressure that you can use. But additionally you need to take care of the following.
2.For the system test of a completed piping system, the test pressure shall not exceed the maximum allowable test pressure of any of the components, like flanges and valves and any other specialty items that are included in the test circuit.
3.As an example, refer to para 2.5 of B 16.5 and para 2.5.3 of B 16.34.
4.In case of B16.5 flanges, you should consider the pr./temp. rating chart and find out the rated pr. At 100 deg.F , multiply it by 1.5 and round it up to next higher 25 psi to get the max. allowable test pressure. This proves to be the limiting factor in many cases.