#1237 - 08/12/03 05:10 PM G-factor for seismic loads
Ed Congdon Offline
Member

Registered: 12/22/99
Posts: 2
Loc: Los Angeles, CA, USA
My piping system for analysis is located in California, seismic Zone 4. In the past I have used .463g for U when performing static equivalent seismic analysis. A consultant says to use .368g for the y direction, and .836g for the x and z direction. Any comments or suggestions?

Top
#1238 - 08/12/03 09:05 PM Re: G-factor for seismic loads
Anindya Offline
Member

Registered: 09/14/02
Posts: 58
Loc: India
Ed,

The bottom line is that the base shear values using static method and the dynamic analysis should match.

Is your project based on IBC 2000? The IBC 2000 gives a more detailed response spectrum method than the previous UBC 1994/1997.You can go through an excellent atricle on this topic in the latest Newletter of COADE ( OCT 2002 ).

Based on the code( IBC/UBC) that you are using for your project, perform a dynamic analysis and check if the base shear matches w.r.t the numbers provided by your consultant.

Since you are from California, the UBC response spectrum ( and also IBC )is very very authentic ( which I would look with doubt for say India ) , so the comparison of static /dynamic base shear coeffients is the nbest method suitable for you to check the authenticity of the data provided by your consultant.

When making the comparison follow the guidelines provided in the technical article I mentioned before.


A.Bhattacharya

Stress Analyst

Bechtel Corporation
_________________________
Anindya Bhattacharya

Top
#1239 - 08/13/03 09:48 AM Re: G-factor for seismic loads
Aziz Mohammad Offline
Member

Registered: 08/12/03
Posts: 4
Loc: overland park,KS
G factor is calculated from Design Spectral Response Acceleration (short period) for the particular site and is usually furnished by the owner. It is also a function of component amplification,response modification,importance factor and the point of support attachment inside the building structure.
_________________________
Mohammad Aziz
Black&Veatch SPC

Top
#1240 - 08/13/03 10:21 AM Re: G-factor for seismic loads
John Breen Offline
Member

Registered: 03/09/00
Posts: 482
Loc: Pittsburgh, PA (& Texas)
Hi Ed,

It also might be a site specific requirement if it is a government facility.

There is MUCH good free info at this address:

http://www.llnl.gov/es_and_h/hsm/doc_22.04/doc22-04.html#27.5

Regards, John.
_________________________
John Breen

Top



Moderator:  Denny_Thomas, uribejl 
Who's Online
0 registered (), 35 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
May
Su M Tu W Th F Sa
1 2 3 4
5 6 7 8 9 10 11
12 13 14 15 16 17 18
19 20 21 22 23 24 25
26 27 28 29 30 31
Forum Stats
12065 Members
14 Forums
16973 Topics
75151 Posts

Max Online: 303 @ 01/28/20 11:58 PM
Top Posters (30 Days)