Posted by: POWER
Firewater Pump - Piping Stress Analysis - 05/06/10 01:24 AM
Hi to all
Please give me ur comments on things to consider for
Firewater Pump - Piping Stress Analysis
Is it recommended to analyse such a system?
thank u
Posted by: POWER
Re: Firewater Pump - Piping Stress Analysis - 05/13/10 01:56 AM
hi
please give ur valuable comments
Posted by: priyan
Re: Firewater Pump - Piping Stress Analysis - 05/16/10 03:14 AM
If you have a Header in your piping System u must calculate.
Because Normally in Oil Field Fire Header We always Maintain 10 Barg Pressure. (It s Depends)
Posted by: STC
Re: Firewater Pump - Piping Stress Analysis - 05/16/10 02:59 PM
If your pump is centrifugal type specified as per API610, the pump nozzle loads needs to be evaluated against the nozzle allowable (API610 table 2-1A or vendor supplied). How can you check the nozzle loads without a formal stress analysis?
Posted by: Tengku_Syahdilan
Re: Firewater Pump - Piping Stress Analysis - 05/18/10 06:09 AM
Dear Power,
You still need to check the Pump Nozzle load, if you have line 3" above connect to rotating pump, then check it by doing stress analysis, just to make sure your load at the nozzle pump does not exceed API 610 or vendor allowable load.