#16150 - 02/21/08 01:34 PM Expansion Loops In A Steam Line
mul211 Offline
Member

Registered: 01/27/06
Posts: 61
Loc: Cincinnati
Say you have 200 ft of 6" SS steam pipe at 350 deg F would you add expansion loops to control the movement or put an anchor in the middle and let the pipe grow out in each direction? I've typically used expansion loops but some clients don't want to spend the extra money for loops if they're not needed. If the desgner says that say a 4.5" movement at the end of the run doesn't create a problem, is a loop really required?

Top
#16154 - 02/21/08 02:33 PM Re: Expansion Loops In A Steam Line [Re: mul211]
Jop Offline
Member

Registered: 12/12/05
Posts: 191
Loc: Florida, USA
The answer to your question rest in the branch lines from the main 6" header.
What are these branch lines (purpose & function)?
What is the size of each?
Where are they located along the main header?
How long are each branch from the main header to the first restriction to lateral movement?
How much movement would you have at each branch under each condition (w/loop and w/middle anchor)?

Check your header out each way and then select the best solution for your project.

_________________________
Jop

Top
#16163 - 02/21/08 05:33 PM Re: Expansion Loops In A Steam Line [Re: mul211]
bom Offline
Member

Registered: 06/23/07
Posts: 285
Loc: Manila, Philippines
4.5" displacement would not create a problem? perhaps in your aplication, but do you have a company standard of maximum pipe thermal displacement? For that long in my experience with steam lines in piperack 100ft to 114ft needs a loop or expansion joint perhaps...

Work with your Senior engineer.

Regards!
_________________________
BOM

Top
#16183 - 02/22/08 11:22 AM Re: Expansion Loops In A Steam Line [Re: bom]
gabionex Offline
Member

Registered: 06/11/07
Posts: 12
Loc: canada
As per previous post, check your client’s flexibility standard or your company’s.
Usually clients accept/reject elimination of expansion loops based on more “serious” reasons (steam hammer!?) and cost comes in secondary; however, if you exceed the maximum allowed displacement, always request a formal deviation from the qualifying standard. Check the MOC (Management of Change) procedure and document properly.

Top
#16198 - 02/23/08 04:54 AM Re: Expansion Loops In A Steam Line [Re: mul211]
Muthu S Offline
Member

Registered: 04/12/07
Posts: 7
Loc: UK
better to avoid unnecessary expansion loops. placing anchor in between the 200ft should be fine. displacements of 2-3" at the ends could be easily absorbed at the unit piping.

Top



Moderator:  Denny_Thomas, uribejl 
Who's Online
0 registered (), 110 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
May
Su M Tu W Th F Sa
1 2 3 4
5 6 7 8 9 10 11
12 13 14 15 16 17 18
19 20 21 22 23 24 25
26 27 28 29 30 31
Forum Stats
12065 Members
14 Forums
16973 Topics
75151 Posts

Max Online: 303 @ 01/28/20 11:58 PM
Top Posters (30 Days)